Since most of us here at KeelyNet are intensely interested in
|
|
becoming totally power independent, I felt the following information
|
|
might be of use in understanding just what are the electrical
|
|
requirements to run your house.
|
|
|
|
It is one thing to dream of the day when we will finally be able to
|
|
build or buy a system to run our vehicles or power our homes. It is
|
|
another to get down to "brass tacks". A one time purchase or lease
|
|
that could be easily maintained and supported for years of reliable
|
|
operation is the goal. This information will show you some of the
|
|
realities.
|
|
--------------------------------------------------------------------
|
|
The following text and specifications are taken from the W. W.
|
|
Grainger and McMaster Carr catalogs.
|
|
--------------------------------------------------------------------
|
|
Typical Electric Tool and Appliance Wattages
|
|
|
|
Equipment Running Watts Maximum VA
|
|
Light bulb (100W) 100 100
|
|
Radio 150 150
|
|
Fan 200 600
|
|
Television 400 400
|
|
Refrigerator (conventional) 400 1200
|
|
Furnace fan - 1.3HP w/blower 600 1800
|
|
Vacuum cleaner 600 1800
|
|
Sump pump - 1.3HP 700 2100
|
|
Refrigerator/freezer combination 800 2400
|
|
6" Circular Saw 800 2400
|
|
Floodlight 1000 1000
|
|
1/2" Drill 1000 3000
|
|
Toaster/Coffeemaker 1200 1200
|
|
Skillet 1200 1200
|
|
14" Chainsaw 1200 3600
|
|
Water well pump - 1/2HP 1400 4200
|
|
Hot plate range (per burner) 1500 1500
|
|
10" Circular Saw 2000 6000
|
|
Water heater (storage type) 5000 5000
|
|
Electric oven 10000 10000
|
|
--------------------------------------------------------------------
|
|
An electrical generator must be properly sized for the load it will
|
|
be called upon to handle. Electric motors are particularly
|
|
difficult for a generator because starting an electric motor
|
|
requires 2 to 3 times its nameplate rating or wattage.
|
|
|
|
|
|
Page 1
|
|
|
|
|
|
|
|
|
|
|
|
While electricity supplied by an electric power company has
|
|
essentially infinite SURGE capacity (limited only by the circuit
|
|
protection provided), a generator is limited by the engine
|
|
horsepower and intertia of the rotating parts. Thus, a current
|
|
surge of short duration can be supplied by a generator, but with a
|
|
current demand of longer duration such as a heavily loaded motor
|
|
starting a high inertia system, can overload a generator possibly
|
|
damaging both the generator and motor. A 3450 RPM air compressor
|
|
motor is a prime example of this type of load.
|
|
|
|
For this reason, when determining the power your generator is to
|
|
provide, it is important to calculate electric motor requirements at
|
|
3 times the running watts to compensate for the surge needed to
|
|
start the motor. With this in mind, the following guidelines can be
|
|
helpful in selecting the right size generator for your application.
|
|
|
|
1. Total the wattages of all small appliances, tools and light
|
|
bulbs to be operated at the same time. Most appliances have
|
|
labels showing wattage (if volts and amps are given, volts X
|
|
amps = wattage). For example, you may wish to operate the
|
|
following equipment.
|
|
|
|
Electric heater 1000 Watts
|
|
Eight 100 Watt light bulbs 800 Watts
|
|
Total 1800 Watts
|
|
|
|
2. Next determine volt-amperes (wattage) requirements of electric
|
|
motors to be operated (e.g. furnace blower motor), remembering
|
|
that the starting requires 2 to 3 times the nameplate or
|
|
running (rated) watts. Thus, if running watts of the motor is
|
|
600, multiply the number by 3 to determine the maximum VA
|
|
needed.
|
|
Running = 600 Watts
|
|
Starting = 600 X 3 = 1800 Max. VA
|
|
|
|
The starting (max.) VA can also be determined by referring to
|
|
the motor code listing which indicates starting KVA per
|
|
horsepower.
|
|
|
|
3. Total watts and VA in Steps 1 and 2 to get the total
|
|
requirements:
|
|
Running Starting
|
|
Step 1 1800 W 1800 VA
|
|
Step 2 +600 W +1800 VA
|
|
2400 W 3600 VA
|
|
|
|
+25% +600 +900
|
|
3000 W 4500 VA
|
|
|
|
4. To allow for anticipated future needs or use of extra
|
|
equipment, add 25% to the total load as in Step 3.
|
|
|
|
5. See performance data charts at the bottom of each generator
|
|
listing for the unit that meets your total load criteria. For
|
|
example, a generator that provides at least 4500 max. VA (No.
|
|
4W108) produces 4600 VA and 4000 watts which meets the load
|
|
required by the example above. A 3000 watt generator should
|
|
not have enough max. VA to start the electric motor load.
|
|
|
|
|
|
Page 2
|
|
|
|
|
|
|
|
|
|
|
|
NOTE: If more than one motor is to be started, start ONE MOTOR
|
|
at a time and always start the LARGEST FIRST. If trying
|
|
to take the entire load of the generator from a single
|
|
receptacle, be sure ampere rating of receptacle is not
|
|
being exceeded.
|
|
|
|
NOTE: Make sure that extension cords used with generators are
|
|
properly sized for load and cord length. Otherwise,
|
|
excessive voltage drops and generator loading may result
|
|
and CAUSE excessive heating of portable power tools.
|
|
--------------------------------------------------------------------
|
|
Motor Code Listing
|
|
Code KVA/HP | Code KVA/HP | Code KVA/HP
|
|
A 0-3.15 | H 6.3-7.1 | R 14.0-16.0
|
|
B 3.15-3.55 | J 7.1-8.0 | S 16.0-18.0
|
|
C 3.55-4.0 | K 8.0-9.0 | T 18.0-20.0
|
|
D 4.0-4.5 | L 9.0-10.0 | U 20.0-22.4
|
|
E 4.5-5.0 | M 10.0-11.2 | V 22.4 & UP
|
|
F 5.0-5.6 | N 11.2-12.5 |
|
|
G 5.6-6.3 | P 12.5-14.0 |
|
|
--------------------------------------------------------------------
|
|
Recommended Extension Cords for use with
|
|
Generators and Portable Electric Tools
|
|
|
|
It is important to use extension cords of adequate current carrying
|
|
capacity when utilizing a generator to operate portable electric
|
|
tools. Undersized cords result in excessive voltage drops and
|
|
additional power plant loading. This also causes excessive heating
|
|
of the portable tool because voltage drop reduces tool capacity.
|
|
|
|
Ampere Rating Wire Gauge @ Cord Length
|
|
50 foot 100 foot 150 foot
|
|
2 18 18 18
|
|
3 18 18 18
|
|
4 16 16 16
|
|
5 16 16 16
|
|
6 16 16 14
|
|
8 16 14 12
|
|
10 16 14 12
|
|
12 14 14 12
|
|
14 14 12 10
|
|
16 12 12 10
|
|
--------------------------------------------------------------------
|
|
In any power generation system, you have several options. You can
|
|
generate power AS YOU USE IT, you can store the power in a battery
|
|
network and convert it with the use of inverters (DC to AC) to run
|
|
your appliances.
|
|
|
|
We all would like to see some kind of virtual flux/ZPE tap, however,
|
|
until such technologies are a reality, we have other options. The
|
|
energy used is still the same, regardless of how it is generated.
|
|
|
|
Personally, I think the first systems must be hybrids, using a
|
|
combination of several technologies. So, as an experimenters
|
|
startup pack, I suggest you download the file GARRETT1.ZIP which
|
|
contains the patent and .GIFs for the Garrett Electrolytic
|
|
Carburetor as used to run a 4 cylinder automobile engine in the 30's
|
|
here in Dallas.
|
|
|
|
|
|
Page 3
|
|
|
|
|
|
|
|
|
|
|
|
The basic principle is to convert water to hydrogen and oxygen, mix
|
|
it with air and explode these intermixed gases to drive an off the
|
|
shelf engine.
|
|
|
|
The idea is to provide the motive force to turn a generator, that
|
|
charges the batteries, then an inverter converts the DC to AC as it
|
|
is necessary to run the house. And we can use the battery
|
|
reconditioning technology that applies a 3.3Mhz frequency to the
|
|
electrodes (3.3Mhz is the sulphur NMR frequency) to cause the
|
|
sulphates to redissolve into the battery acid.
|
|
|
|
Anyway, hope you get the point and will share your experimental
|
|
results with all of us here at KeelyNet!
|
|
--------------------------------------------------------------------
|
|
|
|
If you have comments or other information relating to such topics
|
|
as this paper covers, please upload to KeelyNet or send to the
|
|
Vangard Sciences address as listed on the first page.
|
|
Thank you for your consideration, interest and support.
|
|
|
|